Dec 19, 2000 #1 sildaw Electrical Joined Sep 6, 2000 Messages 1 Location GB Does anybody have any rule-of-thumb guides for elecrical loads for hotels. e.g. kW/room ?
Dec 19, 2000 #2 Guest try 2 kw per room, plus 1 kw per seat in any restaurant(s), plus 6 watts per square ft in any office/conference space. It should be close to about 40%-50% of the main disconnect capacity, as a sanity check. Upvote 0 Downvote
try 2 kw per room, plus 1 kw per seat in any restaurant(s), plus 6 watts per square ft in any office/conference space. It should be close to about 40%-50% of the main disconnect capacity, as a sanity check.
Dec 22, 2000 #3 jbartos Electrical Joined Jan 15, 2000 Messages 6,440 More info is needed. 1. Will it have a commercial kitchen? 2. Underground parking? 3. Etc. Upvote 0 Downvote