Electrical / Insrumentation trays separation distance

Status
Not open for further replies.

MARCOPEREZR

Electrical
May 22, 2009
3
Hello everybody.

I looked over at NEC and didn't find an answer.

Please point me where to find this information, minimun separation distance between electrical (power, lighting, control) cables and instrumentation (F&G, service, J1, J2, J3, ESD, SIS, Telecom, etc) cables in above ground instalations (trays).

Thanks in advance.

Best Regards.

MARCO
 
Replies continue below

Recommended for you

That's because NEC doesn't care if any of your circuits work or not! They just want to prevent fires and to a much lesser extent electrocution.

Because of the various susceptibilities and noise sources that abound you won't find a Standard. You may find some corporate or industry guidelines or rules.

Search in here for "cables separation control".

Keith Cress
kcress -
 
The classifications you list don't mean much in NEC land.

Anything over 1000V must be separated. Below that, you're on your own - use company standards or best practices.

The NEC does require that all cables in a common tray, conduit etc must be insulated up to the highest voltage in use. So if you run 480 V circuits in the tray, everything else must be insulated to that level.

But itsmoked is very correct - the NEC is mainly a fire prevention standard, not an installation specification.

"The more the universe seems comprehensible, the more it also seems pointless." -- Steven Weinberg
 
I have often seen a metal barrier in a tray, this allows you to run HV and LV cables in the same tray with zero spacing.
Roy
 
Thanks for the replies.

The idea is not to run E&I cables in the same tray with a barrier but to use separate trays for each cable types but using the same support (same threaded rod in a hanging arrangement) and I don't know the separation distance between trays and since NEC doesn't have an answer I guess I'll just have to use 300 or 350mm.

Regards
 
MARCOPEREZR,
300 - 350 sounds OK, the trays need enough spacing so you can get your hands in to lay the cables

Roy
 
300 mm is what is used in most European paper mills and steel works. So it is probably fine.

Gunnar Englund
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
 
Yes, 300mm sounds OK, the problem is that the client is requesting a document or specification stating that 300 is enough I can't find such information, I will continue looking.

Regards.
 