raj151857
Electrical
- Sep 27, 2008
- 13
Following document is collective information regarding flashover occurred in Power Control Centre Panel.
Brief of PCC Flashover
No External element was inside the panels.
1] Both Incomer (3200 A) were charged,Buscoupler off & in service.
2] Feeder 3FA 220KW Motor feeder
3] Feeder 3FB Spare 800A Outgoing feeder (ACB Rack Out & No Cable connected on links).Both Feeder 3FA & 3FB are in same vertical Panel.
4] Insulation Value was checked at Motor feeder & found OK (>500 Mega ohms)
5] 220KW Motor was started & flashover Occurred.
Observation after Flashover
A] No Damage was found on Motor feeder.
1] Most affected Part is Contacts of Bottom feeder 3FB connected to vertical bus dropper located on back (Incoming contact of ACB) & Outgoing links connected to Outgoing links. Pics cannot be attached.I can send by mail on request.
2] Entire busbar on Bottom feeder 3FB got blackened & carbonized.
3] Fault was cleared by Motor feeder protection 50/2.
4] CT Ratio 400:1 I>> setting 8.97 A Time 0.01 sec.
5] Motor started from LCS Starting current was 2.16KA, 2.05 KA, 2.16 KA. For 283 milli second after that current in R & Y phase rise to 11.7 KA & tripped on 50/2 protection.
6] No voltage dip was observed.
7] Both the feeders were covered with shrouds, so No possibility of foreign material fall on 3FB feeder.
8] Motor was meggered after flash over and found ok.
I want to know the reason why Flashover occured in bottom spare non energised feeder.
Brief of PCC Flashover
No External element was inside the panels.
1] Both Incomer (3200 A) were charged,Buscoupler off & in service.
2] Feeder 3FA 220KW Motor feeder
3] Feeder 3FB Spare 800A Outgoing feeder (ACB Rack Out & No Cable connected on links).Both Feeder 3FA & 3FB are in same vertical Panel.
4] Insulation Value was checked at Motor feeder & found OK (>500 Mega ohms)
5] 220KW Motor was started & flashover Occurred.
Observation after Flashover
A] No Damage was found on Motor feeder.
1] Most affected Part is Contacts of Bottom feeder 3FB connected to vertical bus dropper located on back (Incoming contact of ACB) & Outgoing links connected to Outgoing links. Pics cannot be attached.I can send by mail on request.
2] Entire busbar on Bottom feeder 3FB got blackened & carbonized.
3] Fault was cleared by Motor feeder protection 50/2.
4] CT Ratio 400:1 I>> setting 8.97 A Time 0.01 sec.
5] Motor started from LCS Starting current was 2.16KA, 2.05 KA, 2.16 KA. For 283 milli second after that current in R & Y phase rise to 11.7 KA & tripped on 50/2 protection.
6] No voltage dip was observed.
7] Both the feeders were covered with shrouds, so No possibility of foreign material fall on 3FB feeder.
8] Motor was meggered after flash over and found ok.
I want to know the reason why Flashover occured in bottom spare non energised feeder.