Hi macgyvers2000;
Teck cable is pretty rugged and resilient.
Teck is often the highest cost option. For temporary duty, I would size the cable based on the connected load rather than the 100 amp service. I would consider disconnecting electric stoves and or hot water heaters if feasible. Protect the cable with a breaker suitable for the cable size you decide on. Don't forget to check the voltage drop, it increases as the size of the cable is reduced.
Specs; The Canadian Electrical Code has a description of the
construction of teck cable. Usually TECK-90, you will want 3 conductor, which will have three equal current carrying conductors and a smaller bare ground conductor. If the ground is frozen you will also want Minus 40 degree rated teck, but that's pretty common in your area.
Teck-90 comes in both aluminum and copper construction.
Be sure to spec the material that you want. A couple of years ago, we needed about 500ft. of teck for a temporary service. We calculated loading and voltage drop and called the office. Our bean counter saved a lot of money by buying aluminum instead of copper. The lights sure dimmed when the big A/C started. Fortunately the installation was for a short time and did not require an inspection.
Another option may be to only power one home at a time. You may accidentally power both for the walk through, by mistake.
Good luck. I'm sunning in the tropics for another few weeks, but I will be back in the land of teck cable and frozen ground in time for breakup.
Bill
--------------------