Thank you very much everybody for your input it is very helpfull and appreciated.
I presumed that the motor should not be much larger than the generator. If mechanical losses in the generator are combined to 2-3% from output of the generator 5.5KW x 3 / 100 = 0.165KW. Mechanical losses in the motor 2-3% from total power 6KW x 3 / 100 = 0.180KW total maximum losses in the gen set are no larger than 0.5KW (0.165 + 0.180 = 0.345KW)
That means that a 6KW motor should easily handle a 5.5KW generator.
What puzzelled me is on a trip to a local hardware store I looked at a GenSet specifications of which are as follows:
5.5KW, 110v, 60HZ, 3600RPM, 1phase
Gas motor 14.7HP x 0.746 = 11KW ??!!
I wonder if anybody knows the reason why a manufacturer would make such a design where the motor is 14.7HP = 11KW which clearly doubles the size of the generator??!!
Is the design of the motor so poor that half of the power the motor produces are lost in it's own mechanical losses?
Thanks,
DVX