gafoorkti;
Please see the excerpt from B16.9 below regarding design of the fitting.
2.2 Design of Fittings
The design of fittings shall be established by mathematical
analyses (e.g., ACME B16.49 for bends) contained
in nationally recognized pressure vessel or piping codes,
or at the manufacturer’s option by proof testing in accordance
with para. 9 of this Standard. In order to meet
design or manufacturing requirements, it is expected
that some portion of formed fittings may have to be
thicker than the pipe wall with which the fitting is
intended to be used. The mathematical analyses, if used,
may take into account such thicker sections. Records of
mathematical analysis and/or successful proof test data
shall be available at the manufacturer’s facility for
inspection by the purchaser.
Unfortunately, ASTM A 234 does not provide any guidance for minimum wall thickness for a elbow, only material specification information.
As I mentioned previously, you need to know the code of construction for installation of this fitting. If the fitting is certified to B16.9 from the supplier, discuss with the supplier the minimum wall thickness.