I wish you had provided a sketch showing the no. of storeys, egress stair storey , seismicity etc.
Apparently the egress stair is steel with RHS stringers .
Below is a worked example calculation based on a imaginary sample data ;
- For the stair body ;
ap=1.0 , Rp=2.50 , z=25ft, h=60 ft , Ip = 1.5, Sds = 0.8g, Wp=5000 lbs
Fp=1760 lbs Fpmax =1.6*Sds*Ip*Wp =9600 lbs Fpmin =0.3*Sds*Ip*Wp =1800 lbs ⇒ 1760<1800 so take Fp=1800 lbs .
This horizontal load should be applied to the mid point of two stringers ( 900 lbs for each one ) or may be applied UDL as @driftLimiter pointed out .
- For Fasteners of egress stairs,
ap = 2.5, Rp = 2.5, Ω0 = 2.5 z=25ft, h=60 ft , Ip = 1.5, Sds = 0.8g, Wp=5000 lbs
Fp=4400lbs Fpmax =1.6*Sds*Ip*Wp =9600 lbs Fpmin =0.3*Sds*Ip*Wp =1800 lbs ⇒1800 <4400<9600 so take Fp=4400 lbs
This load should be applied to the four connections of the stringers .
You may develop spreadsheet for multi storey bldg with egress stairs at every storey.
I hope this respond answers your post.