msm15
Mechanical
- Apr 22, 2010
- 18
I am trying to size up the gas lines for a bunch of 115k btu Furnaces - 115 CFH. and would like to know if the sizing charts in NFPA 54 can be used, and how the pressure loss due to elevation effects things if it does at all.
I will simplify the question as the details are not that important.
Incoming pressure is 6" of water column - roughly .22psi the pipe will be Sch 40 metal, will have run length straight up vertically of 80' with a 115kBTU of 115 CFH furnace at the top (6th floor).
According to the tables - 6.2(a) a 1" would be more then sufficient - being able to supply 119CFH to a distance of 150'
The Architect designing the plans says we cant use those tables and wanted a 2" line just for that heater - that sounds ridiculous and I am quite sure he doesn't know what he is talking about. I would like to do the calcs based off the Low pressure Gas Formula in 6.4.1 but I am not sure what the pressure loss is for Delta H.
Does the elevation really effect things that greatly ?
Thanks
I will simplify the question as the details are not that important.
Incoming pressure is 6" of water column - roughly .22psi the pipe will be Sch 40 metal, will have run length straight up vertically of 80' with a 115kBTU of 115 CFH furnace at the top (6th floor).
According to the tables - 6.2(a) a 1" would be more then sufficient - being able to supply 119CFH to a distance of 150'
The Architect designing the plans says we cant use those tables and wanted a 2" line just for that heater - that sounds ridiculous and I am quite sure he doesn't know what he is talking about. I would like to do the calcs based off the Low pressure Gas Formula in 6.4.1 but I am not sure what the pressure loss is for Delta H.
Does the elevation really effect things that greatly ?
Thanks