pattontom in black, BA in red.
paddingtongreen and BA, in the soil bearing diagram, all axial loads are the same. In diagram in the middle with eccentric load but normal size footing, the column at edge can produce tension in 90% of bottom.
If the column at edge is hinged to the footing, it is an eccentric load. It produces variable compression on the soil near the edge, but cannot produce tension because soil cannot take tension. So it produces a triangular block of compression near the edge. But in the rightmost picture with oversize footing and same axial load with respect to left diagram, the bending and shear and sheer weight of the footing can compensate for the lifting and make it stable.
This is simply not true. This is what SAFE shows.
I don't think so. BA, what do you mean the column has to be designed for bending, it doesn't bend because the 2nd floor has beams that directly connect the left and right side of the lot and all columns connected continuously in upper floors (starting with second) and the floor diaphragms makes it act as one unit.
Draw a Shear Force and Bending Moment diagram for the footing. The moment taken by the column is the footing load multiplied by the eccentricity to the center of column. This is the setup for millions of homes in our country. What do you think is wrong?
I think what is wrong is your understanding of the situation. Anyway. Is it specifically mentioned in the ACI that the column needs to be located inside the kern?
No, it is not nor does it need to be. Next year our structural code which is copied from the USA will be updated. Maybe I can convince the committee to include the kern thing and make all new building permit obey it?
Don't even try because that would be wrong. For that to be true, we need to master the art of combined footings which is quite rare here. For example, the setup I'm doing have not been done by more than 80% of engineers here and they haven't handled such thing before except mostly mat and piles foundation.
No comment on that as I do not know your local practice.
BA. What do you mean of North south wind on the shearwall? I don't have any shearwall, the left and right walls are 6 inches Concrete Hollow Block filled with cement.
An earlier comment of yours stated that the left and right walls are full 6" and I assumed they were shear walls for lateral forces acting in the north-south direction. I am assuming North at the top of your sketch. The back has wall that is 1.5 meters beyond the columns (cantilevered), the front is open as the place would be lease to banks in the future. Also remember the 3 strips of combined footings will be connected to the upper floors solidly. So how would smaller width of the combined footings in each of them overturn the building longitudinally (which is longer than the transverse side) when they are connected as a unit?
The shear walls must be effectively carried down to footing level or some other bracing supplied to prevent overturning of the combined footings about an East-West axis.
pattontom said:
Thanks guys. So I'll use combined footings. Anyway. The rear and back of the ground floor is open and the second floor front and back cantilever 1.5 meters forward and back. Only the left and right side has full 6" thick wall. My tranverse side is weak. I rely solely on the column-beam joints to give strength to the open front and back. Anyone can comment about open story? Are you confident that joints moment frames are enough? I can't use shear walls because the front and back has to be opened. Any suggestions? Thanks.
BA