neeb
Electrical
- Jan 7, 2005
- 2
We are about to install a number of motors (approximately 600kVA each) each driven by a variable speed drive and associated transfomer. The manufacture is recommending that the transfomer secondary is left unearthed (neutral star point not brought out) i.e. an IT earthing system, since the motor is the only consumer off the transfomer. This sounds a little suspect to me as normal practice would be to always earth the neutral to prevent to the voltage "floating" about.
Anybody any experience or thoughts on this?
Anybody any experience or thoughts on this?