goldyvb
Electrical
- May 9, 2007
- 13
Hi All,
We have designed some intrinsically safe instrument loop circuits where the sensor is cabled from the main DCS panel to a field panel just outside the hazardous area (in the safe area) where the intrinsically safe barriers are located. This then supplies the instrument in the hazardous area. There are 3 barriers in this field panel. The two options we have looked at for the termination of the screens are:
(1) Install an insulated terminal underneath each barrier and continue the IS instrument cable screen to the DCS cabinet (via the supply cable screen) where the screen will be terminated to instrument earth (earthed at one point only at the source)
(2) Run a dedicated instrument earth cable (16mm2 earth) from the DCS instrument earth out to the intrinsically safe barrier field panel, install an insulated instrument earth bar in this panel, and terminal all the IS cable screens to it
I am interested in feedback on both options, and whether or not they both meet current Australian/IEC Ex standards? We have used option 2 previously.
Thankyou in advance for your feedback
We have designed some intrinsically safe instrument loop circuits where the sensor is cabled from the main DCS panel to a field panel just outside the hazardous area (in the safe area) where the intrinsically safe barriers are located. This then supplies the instrument in the hazardous area. There are 3 barriers in this field panel. The two options we have looked at for the termination of the screens are:
(1) Install an insulated terminal underneath each barrier and continue the IS instrument cable screen to the DCS cabinet (via the supply cable screen) where the screen will be terminated to instrument earth (earthed at one point only at the source)
(2) Run a dedicated instrument earth cable (16mm2 earth) from the DCS instrument earth out to the intrinsically safe barrier field panel, install an insulated instrument earth bar in this panel, and terminal all the IS cable screens to it
I am interested in feedback on both options, and whether or not they both meet current Australian/IEC Ex standards? We have used option 2 previously.
Thankyou in advance for your feedback