Earthing of neutral on single phase transformer

nbys

Electrical
May 10, 2025
1
HI All
I cannot understand the physics of why a neutral that is ungrounded will be at a higher voltage relative to a live on a single phase transformer lets say a 11kV to 230 V trf . not centre tapped as opposed to when the neutral is grounded
i need to see some diagrams and calcalutions from 1st principles please
it is troubling me
regards
 
Replies continue below

Recommended for you

Well, if the 230V side has no ground reference then presumably the neutral voltage could be anywhere depending on the leakage impedance to ground. I’ve seen similar issues with ungrounded DC systems - typically they float with positive and negative sides equal between ground unless one side has a different ground resistance, like a junction box getting wet.
A 230V system should act similarly - the neutral would be close to ground potential unless the impedances to ground on either leg were different - granted, I haven’t come across an ungrounded 230V single phase system so don’t have direct experience. Several 480V 3 phase systems though.
 