E60 vs E70 welding electrodes

Status
Not open for further replies.

fne

Structural
Joined
Apr 18, 2013
Messages
39
Location
US
Our specs for welding structural steel (buildings) have historically called for the use of E70 electrodes. Recently a contractor has requested the use of E60 for some A36 material citing "matching strength criteria". A little research reveals this is not a new concept. What are other firms doing? Any reason not to allow this with the appropriate check of the weld design?
 
We use E60 for galvanized steel welding. Have not used it for “matching” steel.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
If it has the required strength, and they have the proper weld procedures in place for the joint/electrode combination then structurally it is fine.

My concern would be consistency - is the entire job to be done with A36 steel and E60 electrodes? If higher strength steel/electrodes are required for other parts of the job then I would be inclined to say stick with the E70 everywhere so it doesn't get mixed up.
 
AWS D1.1 Table 3-1 gives compatible base metal/filler combinations. A36 up to 3/4" thick is a Group I metal that can be welded with E60XX electrodes. A36 over 3/4" thick is a Group II metal which can't be welded with E60XX electrodes. My AWS D1.1 is outdated and your specific project may not be using AWS D1.1.
 