We have Dual Stand alone UPS ( similar to the below picture) from which both the single and dual cord loads are to be fed.
The single corded loads are fed via STS and the dual corded loads are fed via two separate cables from the UPS A & UPS B.
For this system, the backup time of the battery banks A & B is considered as 50% of the total backup time according to the client spec.
It means, for a load with an autonomy of 30 mins, each battery bank is sized only for 15 minutes for that particular load.
If both the AC Mains and the Bypass power input fails in both the UPS, the battery has to power the loads. I'm planning to use Timers to trip the Circuit Breaker once the autonomy time (50% per each battery bank) is elapsed.
The issue here is, how do I ensure that load cuts off in the specified autonomy time when fed from the batteries? I do not want one battery bank to drain completely.
For the dual corded loads - Both the UPS A & UPS B will have its own circuit breakers- how the scheme for autonomy timer activation and cut off of loads to be implemented. Do I need to set the timer at 30 mins or at 15 mins for the particular loads?
For single corded loads - Do I need to set the timer in STS?
Thank you all!
The single corded loads are fed via STS and the dual corded loads are fed via two separate cables from the UPS A & UPS B.

For this system, the backup time of the battery banks A & B is considered as 50% of the total backup time according to the client spec.
It means, for a load with an autonomy of 30 mins, each battery bank is sized only for 15 minutes for that particular load.
If both the AC Mains and the Bypass power input fails in both the UPS, the battery has to power the loads. I'm planning to use Timers to trip the Circuit Breaker once the autonomy time (50% per each battery bank) is elapsed.
The issue here is, how do I ensure that load cuts off in the specified autonomy time when fed from the batteries? I do not want one battery bank to drain completely.
For the dual corded loads - Both the UPS A & UPS B will have its own circuit breakers- how the scheme for autonomy timer activation and cut off of loads to be implemented. Do I need to set the timer at 30 mins or at 15 mins for the particular loads?
For single corded loads - Do I need to set the timer in STS?
Thank you all!