ajk1
Structural
- Apr 22, 2011
- 1,791
ACI 318 requires that the length of the drop panel parallel to the span, from support centreline to drop edge, be at least 1/6 of the span length(at least the ACI 2008 edition does - that is the latest edition that we have on our office library).
CSA A23.3 does not have this requirement.
Question: Does anyone know why ACI has this requirement?
CSA A23.3 does not have this requirement.
Question: Does anyone know why ACI has this requirement?