Here is the soil report:
DRILLED PIERS
The design and construction criteria presented below should be observed for a straight-shaft pier foundation
system.
1. Piers should be designed for an allowable end bearing pressure of 23,500 psf and a skin friction of 2,350
psf for the portion of the pier in bedrock. Uplift due to structural loadings on the piers can be resisted by
using 75% of the allowable skin friction value plus an allowance for pier weight.
2. Piers should also be designed for a minimum dead load pressure of 5,000 psf based on pier end area only.
Application of dead load pressure is the most effective way to resist foundation movement due to swelling
soils. However, if the minimum dead load requirement cannot be achieved and the piers are spaced as far
apart as practical, the pier length should be extended beyond the minimum bedrock penetration and
minimum length to mitigate the dead load deficit. This can be accomplished by assuming one-half of the
skin friction given above acts in the direction to resist uplift caused by swelling soil and/or bedrock near
the top of the pier. The owner should be aware of an increased potential for foundation movement if the
recommended minimum dead load pressure is not met.
3. Piers should penetrate at least 5 feet into the competent bedrock with a minimum pier length of 25 feet
recommended. The requirements for minimum penetration and minimum pier length should be met.
4. All piers shall be reinforced their full length with steel rebar. The pier reinforcing shall be designed to resist
the tension resulting from the maximum uplift pressures. No less than 1% of the steel based on the pier end
area shall be used. The pier reinforcing steel shall extend into the foundation wall a sufficient distance to
fully develop the bars in tension.
5. The drilled piers should be a minimum of ten inches in diameter. The pier length to diameter ratio should
not exceed 30:1. The recommended diameter must be maintained at the top of each pier hole. We
recommend the use of cylindrical cardboard forms to maintain the diameter of the top of the pier hole and
to prevent mushrooming.
6. The drilled pier holes shall be cleaned of all loose material and filled immediately with concrete to prevent
sloughing of loose soil or infiltration of water. Based on the exploratory borings we do not anticipate
encountering water during drilling of the piers. However, if water is encountered during the drilling it
should be removed prior to placement of the concrete. If the water cannot be removed or prevented with the
use of temporary casing and/or dewatering equipment prior to placement of concrete, the tremie method should be used after the hole has been cleaned. In no case should concrete be placed in more than 3 inches
of water unless placed through an approved tremie method.
7. Concrete used in the piers should be a fluid mix with sufficient slump, so it will fill the void between
reinforcing steel and the pier hole. We recommend a concrete slump in the range of 5 to 8 inches be used.
The concrete should be designed with a minimum 28-day compressive strength of 3,000 psi.
8. A representative of the geotechnical engineer should observe pier drilling operations on a full-time basis to
assist in identification of adequate bedrock strata and monitor pier construction procedures.
9. A minimum four-inch void form shall be placed under the foundation grade beam walls between the drilled
piers.