From an AISC article (for this building the 1" drift at crane level suggested below will be a killer):
Lateral Stiffness for Industrial Buildings with Cranes
Drift criteria for buildings with cranes are not only dependent upon the choice of wall system, but also upon crane movements. For pendent-operated type crane systems, buildings with calculated wind drift ratios of H/100 have performed. However, crane movement can generally be observed. A structure which is this flexible should be described to the owner beforehand so he is not surprised to see his structure move and rattle when the crane is in use. It is suggested, for cab-operated cranes, that building lateral drift be limited to H/240 for both crane loads and wind loads.
In addition, the lateral sway at the elevation of the crane runway should be limited to roughly one inch. Structures supporting computer-controlled cranes will probably require more restrictive tolerances. Although not a drift criteria, it should be mentioned here that it is not recommended to tie masonry walls into crane column steel because of the frequent movement of the columns due to crane action.