Dear Mr. nhcf (Electrical)(OP)2 Dec 22 17:43
" .... #1. Is there an IEEE or similar standard for recommended max voltage drop on a 480 V distribution system during a motor start?..... we can figure out what the transient voltage is, but I'm not sure of what voltage transient is considered too low. ... #2. I've assumed a 15% drop is acceptable, but don't have a good basis for that".
#1. In the US, NEC is the Law. But, I was unable to locate any mention of the allowable (transient) voltage-drop [during starting].
I would assumed that it depends on the motor (transient) torque at lower voltage SHALL be > the load torque in order to accelerate within 10, 20 ---30s, i.e. the limits of the motor and the thermal over-load setting. Note: (a) the (motor torque) is very much lowered when the [source voltage is < the rated]. (b) the (load torque) is [independent of the source voltage].
#2. It is dependent on the motor (kW) rating and the load torque characteristic. The motor torque (with transient lowered voltage) shall be > than the load torque, and able to speed up within the time limit of the motor. In general, the (transient voltage-drop) not exceeding 15% [during starting] would be fine.
#3. FYI: (a) in case that transient VD is too much, consider connect the (contactor coil supply) from a UPS source, or use a DC coil, or electronic controlled coil; which are less sensitive to the voltage.
(b) An IEC AC3 rated contactor would be fine, i.e. without plugging/inching (see IEC for definition of AC3 application).
Che Kuan Yau (Singapore)