Dear Waross,
The unit is fed from the nearest distribution substation with a 22kV supplyAt the outdoor - both at the distributor point and at our receiving point we have horn gap fuses of 60 and 30 amps respectively.This is received by us at the outdoor and though underground cable taken to Group control OCB.
.
From here through HT bus tappings are taken for Dsitribution OCB, two 950kv/560 secondary voltage and one 900kv /560 transformers MOCBs..From the distribution OCB there is one UG cable to HV SSB which has HRC bottle fuse .There is one u/g cable from SSB(Sub swithcing board) to the 1000kVA /433Vdistribution transformer.
All auxiliary supplies like blowers , cleaning equipment, sand plant are fed from this distribution transformer.Also the control supply to the panels for operating the furnaces through the other transformers is from this 1000kVa transformer.
The unit was closed for 4 years and after checking healthiness of transfomers, cables and transformer oil checks, the unit was restarted.
After one month of operation, on a night of heavy rain, the first fuse blow out occured on the B phase horn gap fuse at our end outdoor and also at distributor end and their feeder tripped with earth fault indication in their settin of 120 milliseconds.
Suspicion was placed on the 1000kVa transformer as its Insulation resistance was found to be 6Mohms.
The next step was to check and replace the oil, take the core out for inspection and all these were done while a spare 350kVA transformer was brought in and put into service. Again the fuse got blown in B fuse.
The suspicion was on cable between ssb and 1000 kvA transformer and this was changed from the old paer insulated cable to XLPE cable.
Now when the power was resumed and after 10-12 hours of operation, the Y phase both outdoor fuses and the feeder ACSR conductor got cut.
By this time the two other UG cables were relaid with new XLPE cables, the 100kVa transformer sent outside was found to have a Body to LV side arc and therefore repaired, oil checked, IR value measured and brought back into service.
After this on restoring operations, B phase both outdoor fuses and ACSR conductor got cut and feeder tripped at the distributor end.
They were replaced and now we changed to a different furnace. The previous furnace was Medium frequency induction melting and a Main frequency furnace was brought into service.
After 18 hours of warm up and when increasing power to 300 Kw the fuses got blown again.
Now we are analysing the problem and consulted some experts also.
Their views.
1.Our indoor relays are analog and response time is slower than distribution end and needs to be replaced.
2.Horn gap fuses ends are nearer to other pole lements and even after fuse blown arcing is causing distribution side feeder trip through earthfault.
3.Furnace transformers tap chaningers and core have to be checked.
4.Grading of fuses has to be done.
Please see if all these inputs can help you give us your suggestions.