I am working on a water distribution line for a small subdivision of 11 homes. The architect has been working with the municipality and they have asked for a 6" DI line to the fire hydrant. I was planning on designing the line to the fire hydrant with a 2" blow off assembly for dead end systems. The architect has asked me to run the line on past the fire hydrant but what I was taught is that I cannot do that on a dead end system of less than 1,000 foot of run. That can only be done on a loop. Any input????