- Jul 7, 2007
- 8
I retrieved some recloser data yesterday for one of the feeders. The data was showing
Phase A: PF=0.95, kW=258, kvar=85, KVA=269
Phase B: PF=0.56, kW=237, kvar=-346, KVA=421
Phase C: PF=0.51, kW=213, kvar=-356, KVA=416
The power factor on b and c phases were of some concern, and was considering a cap bank. What size cap bank would be ideal for this case. I was thinking of a 300 KVAR bank. I have never dealt with capacitor banks on the distribution feeder level, so any of your input is appreciated.