- 68
I'm currently involved in evaluating a distributed generation proposal for a utility. It includes 600kW of 1-ph synchronous machines connected to a long 1-ph line at 16kV (p-n). This line is protected by a 1-ph recloser.
The gen owner is proposing the normal set of protection (overcurrent, under/over voltage, under/over frequency).
For anti-islanding, as required by IEEE-1547, nominally the installation should provide transfer trip to the local recloser as the size of the generation is around the same size as the load supplied from the recloser.
The customer is instead proposing to set the generation to run at unity power factor and to use reverse VAr sensing to trip the generation if any VArs are output from the generation to support local loads (normally the VArs would be provided by the distribution system).
Has anyone seen reverse VAr sensing used for anti-islanding?
It seems like a simple approach that avoids the need for transfer trip capabilities. Can you see any drawbacks to this approach?
The gen owner is proposing the normal set of protection (overcurrent, under/over voltage, under/over frequency).
For anti-islanding, as required by IEEE-1547, nominally the installation should provide transfer trip to the local recloser as the size of the generation is around the same size as the load supplied from the recloser.
The customer is instead proposing to set the generation to run at unity power factor and to use reverse VAr sensing to trip the generation if any VArs are output from the generation to support local loads (normally the VArs would be provided by the distribution system).
Has anyone seen reverse VAr sensing used for anti-islanding?
It seems like a simple approach that avoids the need for transfer trip capabilities. Can you see any drawbacks to this approach?