Ohm's Law
High voltage networks in rural areas in UK are generally radial.
Power flow is from HV substation then say a 5 mile overhead line with small transformers to low voltage at each customer (think of a series of small farms). The designer expects the HV voltage to decrease with distance, due to line resistance and current flow.
The last farm then builds a digester and installs a gas engine generator set to consume the methane given off by the digester. This could be at a kw rating several times the previous combined load of all the farms, so these loads will be fed by the generator and the surplus exported through the substation.
When the generator is connected to the mains at low voltage at the last farm, the only way to push power into the mains is to raise the voltage at the farm end above that at the substation. So the original voltage drop pattern is reversed.
This may cause problems at the farms along the overhead line.
There are solutions to this, but that’s the basics of it. (omitting a lot of things like power factor of the generator, and moving the point where the generator controls its voltage from generator terminals to a point along the line)
Davidbeach said much the same thing, but I ramble on a lot.