I have distance protection relay used for 33KV radial line around 80 KM long with more than 150 Distribution transformers.
this relay have been operating by Zone-1 many times at energization due to high inrush current 800 A while the maximum feeder load is 200 A.
to avoide this situation we usually open at the middle of the line and energize then we close.
my question: I understand the effect of inrush current in overcurrent operation, can any one explain its effect on distance relay?
thanx