Dear Mr. PKJENNY
Q. When I do a fault discrimination analysis, if I have a final circuit of 32A 1ph MCB with an immediate 400A 3ph upstream MCCB, do I still need to detail check the discrimination, or, from the ratings of the upstream and downstream breakers I can already told discrimination is achieved?
A. With 400A up-stream and 32A down-stream would achieve discrimination on "over-load". But NOT necessary covered the "short-circuit kA " level of the branch feeder.
FYI: The difference between "over-load" and "short-circuit" :
a) "over-load" is on a " healthy " circuit when the current increases exceeding 32A to say up to 400A. Discrimination is achieved i.e. the 32A is going to trip while the 400A remained closed.
b) "short-circuit" is when there is a "fault" where the short-circuit current can reach up to say 20...50kA... Under this circumstance, a "full discrimination may be achieved up to say 10kA i.e. 32A opens while 400A remain closed. But, [discrimination failed] at say 30kA i.e. both the 32A and the 400A trip open.
c) most MCCB and MCB manufacturers publish discrimination tables showing full or no discrimination up to certain kA.
Attention: The tables are NOT suitable for breakers of different manufacturers, unless specifically stated.
Che Kuan Yau (Singapore)