Greetings,
Google is failing as usual, (lately).
I've got a pneumatic cylinder with an internal slide pot for extension length monitoring.
I have an AB PLC analog-IN that is monitoring the cylinder.
The Problem: Hideous nonlinear results. Examining the the various data sheets shows that the cylinder is supposed to only feed into a 1M ohm or higher input. The PLC is spec'd at 200K input impedance.
What I'm hoping to find is a plain old buffer amp in a DIN mount housing so I can drop these things into the existing system between the cylinders and the PLC.
Any ideas?