I think they are refering to an AC hipot, vs DC Hipot. Generally to test the breaker you megger it, then to see if the vacuum is in the bottles the bottles are hipoted. They recommend AC though DC can be used. See the manual for voltage levels. The vacuum bottles I have found bad were found with a 5kV megger, it looked ok at 2.5kV, but showed bad at 5kV. Generally the levels they recommend are about 40kVDC across the bottles.