- Mar 12, 2005
- 16
Hi All,
I have a DEG whose Cranking motor current requirement at firing speed is = 1000A DC.
How would I size the Cable for this?
(Cable to be laid between the Battery terminals to the Cranking motor terminals).
I plan to use XLPE Insulated 1 Core cables.I have sizes of 50mm2,95mm2,120mm2 and 150mm2.
Length of cable from battery terminals to Motor terminal=20 meters.
Please advise.
Thanx in advance
I have a DEG whose Cranking motor current requirement at firing speed is = 1000A DC.
How would I size the Cable for this?
(Cable to be laid between the Battery terminals to the Cranking motor terminals).
I plan to use XLPE Insulated 1 Core cables.I have sizes of 50mm2,95mm2,120mm2 and 150mm2.
Length of cable from battery terminals to Motor terminal=20 meters.
Please advise.
Thanx in advance