bender36
Structural
- Mar 5, 2007
- 12
Dear colleagues,
We are facing a problem in understanding and applying the ACI 318M-02 for our project. It is the first project we do acc. ACI. It would be very nice if somebody can help us:
Problem: anchorage of reinforcement at joints / development of positive moment
12.11.1. (…) … such reinforcement shall extend into the support at least 150mm.
12.11.2 When a flexural member is part of a primary lateral load resisting system, positive moment reinforcement required to be extended into the support by 12.11.1 shall be anchored to develop…
In our design, we have lots of continuous beams on columns and continuous grade beams on piles. Even if we apply all load combinations including earthquake & wind, the moment envelope shows no positive moments at connection points beam-column or beam-pile cap.
Acc. 12.11.1 we have to extend ¼ of the positive moment behind the face of the beam by 150mm. Now, there is this clause 12.11.2. I understand that our frames and grade beams carry the lateral loads into the ground – so they are part of a primary load resisting system.
Question: Is it like this?
What is then a secondary lateral load resisting systems ?
When are 150mm for restraint beams / continuous beams sufficient?
Thank you very much and best regards from Germany !
MARTIN
We are facing a problem in understanding and applying the ACI 318M-02 for our project. It is the first project we do acc. ACI. It would be very nice if somebody can help us:
Problem: anchorage of reinforcement at joints / development of positive moment
12.11.1. (…) … such reinforcement shall extend into the support at least 150mm.
12.11.2 When a flexural member is part of a primary lateral load resisting system, positive moment reinforcement required to be extended into the support by 12.11.1 shall be anchored to develop…
In our design, we have lots of continuous beams on columns and continuous grade beams on piles. Even if we apply all load combinations including earthquake & wind, the moment envelope shows no positive moments at connection points beam-column or beam-pile cap.
Acc. 12.11.1 we have to extend ¼ of the positive moment behind the face of the beam by 150mm. Now, there is this clause 12.11.2. I understand that our frames and grade beams carry the lateral loads into the ground – so they are part of a primary load resisting system.
Question: Is it like this?
What is then a secondary lateral load resisting systems ?
When are 150mm for restraint beams / continuous beams sufficient?
Thank you very much and best regards from Germany !