The detail you describe is on most drawings.
I like GE's statement - "The voltages reach a positive maximum in the order T1, T2, T3." No confusion on CCW or CW, viewed from turbine end or collector end. But I have had generator drawings showing "ABC, T1, T2, T3 rotation" where the gas turbine spun the rotor in the opposite direction from "standard" so the electrical drawing (and my buswork) was wrong.
Another drawing detail that is useful is a view looking at the generator terminals saying something like "Viewing the bus leads as they exit the terminal enclosure, the phase sequence is T1, T2, T3, right, center, left."