Chapter 14 is not so clear for me,I found this part in table 14.4.2.2:
(g) Smoke detectors
(1) In other than one- and two-family
dwellings, system detectors and single- or
multiple-station smoke alarms
Smoke detectors/smoke alarms shall be tested in place to ensure smoke
entry into the sensing chamber and an alarm response. Testing with smoke
or listed aerosol, acceptable to the manufacturer of the aerosol or the
manufacturer of the smoke detector/smoke alarm and identified in their
published instructions, shall be permitted as acceptable test methods.
Other methods listed in the manufacturer’s published instructions that
ensure smoke entry from the protected area, through the vents, into the
sensing chamber shall be permitted.
Any of the following tests shall be performed to ensure that each smoke
detector is within its listed and marked sensitivity range:
(1) Calibrated test method
(2) Manufacturer’s calibrated sensitivity test instrument
(3) Listed control equipment arranged for the purpose
(4) Smoke detector/control unit arrangement whereby the detector causes a
signal at the control unit when its sensitivity is outside its listed sensitivity
range
(5) Other calibrated sensitivity test method approved by the authority having
jurisdiction
::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::::
-By the way, we are using intelligent Siemens smoke detectors.
-This paragraph says "each smoke detector" but the tests that follow seem that shall be done at the factory?