shamu08 said:
1-why the zone is pressurized with +2400 cfm
2-if you look at the office room the supply air =600 cfm and the return air =500 cfm from where he get this return air flow rate?
1) First thing I'm noticing in the table is no OA. Including OA will change the amount of pressurization.
2) You need to look at each room individually and the entire zone/building simultaneously.
The excess air from the offices and waiting rooms has to go somewhere, similarly the toilets (which are negative) need to get air from somewhere.
You need to consider where and how the air is moving throughout the zone. Not all the excess air in the offices is going to escape to the outside, some of that is going to go to corridors or other adjacent spaces including the toilet exhaust and eventually to the outside.
shamu08 said:
so, in case we have a positive pressure space, how to calculate the leakage air (transfer air) through the door undercut and air gaps?
Back to my first reply and conservation of mass. The air HAS to go somewhere. There may be a period of time where it doesn't, and the air pressure in the space will increase (like blowing up a balloon), but eventually the air will find a way out, else something eventually breaks. In the long run, the air WILL get out of the space.
When looking at a room in the zone you have SA and RA for air in/out.
Then for the zone you have OA and EA as the air in/out.