Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

definition

Status
Not open for further replies.

nsizwa

Electrical
Jun 5, 2003
1
what does 5 and 10 imply in the 5p10 ct
 
Replies continue below

Recommended for you

5p10 CT
rating indicates accuracy limit factor of CT
P indicates CT should used for protection purpose (i.e. for feeding protective relays.
digits 5 & 10 indicate -- error in secondary o/p will within 5 % evenif current flowing through primary is 10 times rated current

hopr this will satisfy your requiremenrt.
 

For more information you can read:

- IEEE Std C57.13 (IEEE Standard Requirements for instrument Transformers)

- IEEE Std 242 (IEEE Recomended practice for protection and coordination of industrial and comercial power systems)

Good luck!
 
Suggestion: 5p10 ct is not ANSI/IEEE categorization of CTs. Check UK and Europe.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor