Here's a lead for you. I've used these United Electric switches before and one model has ATEX rating, and it isn't clear to me whether it is EXP rated or IS rated. But it's a commercially available temperature switch that will handle 5A.
See page 8 of the 16 page pdf for the 12 temperature switch
See page 11 for the M405 ATEX rating option, & the M423 ATEX junction box,
Maybe you'd need that M460 external grounding screw
If I understand your app, you need the internal panel temperature to be monitored.
It looks like this switch (like their others) can have an integral bulb sensor, for local monitoring, or a bulb on a capillary tube for remote temp monitoring (Mount the switch 6' from the bulb.)
I've worked with these switches for US EXP applications, and I recommend the M201 (factory setting) option for ease of construction - whoever installs it takes it out of the box, wires it up and they're done. It's too easy for contractors/assemblers/installers to overlook the calibration or setting of the switch. (although I've only used the pressure models not the temperature models, presumably temperature can be factory set as well).
They have other models of switches, many of which are FM Class 1 Div 1 for EXP, but I'm not sure whether the others have the ATEX rating. Having spec'd this Spectra model recently, I recalled the ATEX option on the Spectra 12, but I'm sure their distributor can help you out to see if another one might be more suitable.
Dan