ARLORD...you mentioned one thing that caught my attention...."they would like to fabricate the trusses themselves". A 70-ft span, heavily loaded truss is not something that "amateurs" should take on just to save a few bucks(I'm assuming from your post that your client does not fabricate trusses on a routine basis). You will have complete joint penetration splices for the top and bottom chords, not to mention a bunch of out of position welding. Make sure in your design you call for such things as welding in accordance with accepted standards (for the US...AWS D1.l), that all welding be inspected by a Certified Welding Inspector or qualified Special Inspector, and that all welders be certified to the particular standard, process, and positions to be encountered.
Bobber1...as for slotted holes in the joist, they are often just for erection, but even so, if they are tightened to any reasonable tension (snug tight plus 1/2 turn or similar) they are not likely to slip under the relatively small lateral bracing loads required. If for diaphram, I would weld them or require tensioning in accordance with AISC requirements for a slip critical connection.
As for bottom chord bracing, not necessary except for uplift as many have noted. For uplift, consider using the guidelines of the Steel Joist Institute for deep, long span joist girders.