Custom plate washer to increase Appendix D capacity

Status
Not open for further replies.

precast78

Structural
Aug 12, 2013
82
On appendix D, the ANC is calculated from the center of the bolt. If I add a thick custom washer, is there a way to increase this number? I feel like my ANC should be higher? Does Appendix D cover this anywhere?
 
Replies continue below

Recommended for you

I only have my ACI 318-05 at home with me. I'm almost certain that 318-08 allows you to calculate Anc starting from the edge of your plate washer, not the center. I've never used the provision, but I'm almost certain it's there.
 
I've done this when I needed a ductile failure of the anchor rods. Just make sure the plate can handle the uplift load in bending, but that shouldn't be too difficult to achieve.
 
You can use a little tiny washer if you put it and the head of the anchor bolt at the bottom of the footing and calling it a through-bolt, which isn't covered by App D.
You will have to excavate a pocket around the head of the anchor to provide adequate concrete corrosion cover. But this way, you can avoid App D altogether.
 