Jul 16, 2009 #1 Bluenoser337 Electrical Joined Mar 27, 2003 Messages 83 Location CA There is a single current transducer with all 3 phases passing through it, on a pump supply. What is that detecting or measuring? Thanks!
There is a single current transducer with all 3 phases passing through it, on a pump supply. What is that detecting or measuring? Thanks!
Jul 16, 2009 2 #2 roydm Industrial Joined Jan 29, 2008 Messages 1,052 Location CA Ground Fault, with no leakage to ground all three phases are in ballance resulting in zero secondary current. A leakage to ground puts the phases out of ballance resulting in a secondary current. Upvote 0 Downvote
Ground Fault, with no leakage to ground all three phases are in ballance resulting in zero secondary current. A leakage to ground puts the phases out of ballance resulting in a secondary current.
Jul 16, 2009 Thread starter #3 Bluenoser337 Electrical Joined Mar 27, 2003 Messages 83 Location CA Thanks roydm!!!!!!!!!!!!!!!!!!!!!!!!!!! Upvote 0 Downvote
Jul 16, 2009 #4 tayyab1020 Electrical Joined Jul 10, 2002 Messages 12 Location OM Is it current transducer or current transformer. If it is current transformer then it is called Ring Core current Transformer. I don't know about any such transducer. Upvote 0 Downvote
Is it current transducer or current transformer. If it is current transformer then it is called Ring Core current Transformer. I don't know about any such transducer.
Jul 17, 2009 Thread starter #5 Bluenoser337 Electrical Joined Mar 27, 2003 Messages 83 Location CA tayyab1020....it turns the current measurement into a proportional 4-20mA signal for connection to a PLC. Upvote 0 Downvote
tayyab1020....it turns the current measurement into a proportional 4-20mA signal for connection to a PLC.