There is a single current transducer with all 3 phases passing through it, on a pump supply. What is that detecting or measuring? Thanks!
 
Ground Fault, with no leakage to ground all three phases are in ballance resulting in zero secondary current.
A leakage to ground puts the phases out of ballance resulting in a secondary current.
 
Is it current transducer or current transformer. If it is current transformer then it is called Ring Core current Transformer.

I don't know about any such transducer.
 
tayyab1020....it turns the current measurement into a proportional 4-20mA signal for connection to a PLC.
 