current with reactor 972 amps
current without reactor 964 amps
In comparison to other effects such as voltage change, harmonics and capacitor tolerance, the reactor does not affect current much.
However, do be aware to include the reactor for calculations on a voltage differential scheme. We have a 115 kV bank that can be either 45, 67 or 112 MVAR with a 5 mH reactor. When it is switched from one size to another the drop in current flow through the reactor will cause a lower the voltage measured across the midpoint of the capacitor bank. Going from memory, it seems like the voltage change is about 1/4th that of a blown fuse. Not enough to cause a misoperation by itself, but it does eat into the safety factor.