Jul 9, 2014 #1 dfdt Electrical Joined Sep 10, 2002 Messages 118 Location AU Can someone explain why distance relaying is generally faster than line current differential scheme for in zone faults.
Can someone explain why distance relaying is generally faster than line current differential scheme for in zone faults.
Jul 9, 2014 #2 davidbeach Electrical Joined Mar 13, 2003 Messages 9,551 Location US No need to wait for communications from the other end. Upvote 0 Downvote
Jul 12, 2014 Thread starter #3 dfdt Electrical Joined Sep 10, 2002 Messages 118 Location AU thanks David Upvote 0 Downvote
Jul 14, 2014 #4 odlanor Electrical Joined Jun 28, 2009 Messages 689 Location BR current differential scheme is a unit-protection. distance relaying needs telecommunication to be a unit-protection. I did not understand David post. Upvote 0 Downvote
current differential scheme is a unit-protection. distance relaying needs telecommunication to be a unit-protection. I did not understand David post.
Jul 14, 2014 Thread starter #5 dfdt Electrical Joined Sep 10, 2002 Messages 118 Location AU What David meant was that in order to make a Trip or Restrain decision, the current diff scheme must wait to receive information packets from the remote end via comms. network which could either be via multiplexer or direct fibre Upvote 0 Downvote
What David meant was that in order to make a Trip or Restrain decision, the current diff scheme must wait to receive information packets from the remote end via comms. network which could either be via multiplexer or direct fibre
Jul 15, 2014 #6 cranky108 Electrical Joined Jul 23, 2007 Messages 6,293 Location US Assume this is line differential, and not bus or transformer differential. Upvote 0 Downvote
Jul 15, 2014 #7 ScottyUK Electrical Joined May 21, 2003 Messages 12,915 Location DE Check the OP. ;-) Upvote 0 Downvote
Jul 15, 2014 #8 odlanor Electrical Joined Jun 28, 2009 Messages 689 Location BR Sorry for my ignorance. What do you mean: Check the OP? Upvote 0 Downvote
Jul 15, 2014 Moderator #9 waross Electrical Joined Jan 7, 2006 Messages 28,794 Location CA OP> original poster or original post. Bill -------------------- "Why not the best?" Jimmy Carter Upvote 0 Downvote