Well, maybe, yes, many, it depends, possibly not: If you want a reasonable answer then include some pertinent data.
Sizes?, secondary current?, calibration?, burden (rated and actual)?, at what PU of rated load do you see inaccuracy?, What are you using the measurement for?
A measurement class CT should be accurate to around 200% of rated current. A protection class CT may be inaccurate at low current but will not saturate until a much higher current than a metering class CT.
If you are attempting to determine the kW of a load with a significant inductive or capacitive component with voltage and current alone, then Google "Power factor".