The CT will be (is required to be) in accuracy class up to the rating factor, meaning that with a rated primary current of 20A and a rating factor of 2.0, the CT will be accurate up to 40A primary current...assuming the CT has a metering accuracy class. In fact, the accuracy will most likely be better at 35A than 20A primary. The CT's accuracy will improve up to the point that it starts to saturate, which by definition must be above the rating factor.
As for the points on the VA rating...
I don't believe the way is the IEC and other standards define burden in terms of VA is the best. I believe the IEEE/CSA method of defining CT burden as an impedance at a particular power factor is the best. Mainly because folks get confused at believe that the burden in terms of VA must vary based on secondary current. Please note that the VA rating is based on the rated secondary current...i.e. a VA rating of 15 VA with a 1A secondary is a 15 ohm burden.
For the CT originally inquired about, the CT is still accurate up to the rating factor of 2.0. The applied burden is still 15 ohms. It's not proper for CT ratings to say with a 2A secondary (RF of 2.0) that the burden imposed on the CT is 60 VA (2^2 * 15) and therefore the CT is out of accuracy. It's best to think of everything in ohms based on the rated sec current and VA rating.