Ihsan Abbas Oudah (Electrical)(OP)28 Oct 23 18:31
"...can I use CT accuracy class C800 for differential protection? Transformer data 11.5/6.6 kV ,25 MVA"
You had already received numerous learned advice. I wish to point out the CT requirements for Transformer differential protection; for your consideration.
1. CT basic requirements:
a)secondary I1 = I2 approx. Phase angle 1 = phase angle 2. Note: modern microprocessor relay can have these differences modified/matched by programming.
b) for through-fault stability, knee-point voltage Vk1 = Vk2 under system short-circuit kA level. Note: independent of the exact magnitude of the voltage.
c) the CT1 internal resistance + external resistance = CT2 internal resistance + external resistance approx. Note: modern microprocessor relay can have these differences modified/matched by programming.
d) refer the relay OEM CT selection recommendation.
2. Additional information: There are two sets of CTs and these are usually located some distance apart. Do NOT earth them locally. Wire the insulated earthing wires to a common point isolated from earth. Connect this ONE point to the Earth.
3. Opinion: as whether suitability of a C800 is dependent on fulfillment of above mention conditions.
3.1 Most recent microprocessor relays are designed to accept CT IEC 5P20 with programming to match the differences.