Crumb Rubber Question

Status
Not open for further replies.

scitanul001

Civil/Environmental
Dec 6, 2006
2
We're looking to help out one of our clients. They have a waterline that is approximately 30" below finished grade. They are requesting a 3"-4" rigid insulation (about an R-3 insulation rating) material to be laid over the top after we excavate down to about 8"-12" above the water line. My question is; can anyone point me in a direction of obtaining an R value for 12" thick of crumb rubber? I need to quantify the R value to the client indicating that the crumb rubber will offer better insulation than the rigid insulation.

Thanks in advance for your responses.
 
Replies continue below

Recommended for you

Looks like a reasonable value for the 12" thickness is R = 7.
See page 2 of "Civil Engineering Application of Tire Shreds" for the following
The thermal conductivity of tire shreds with a 3-in. maximum size is about 0.14 Btu/hr-ft-°F. This is seven times better than soil, which typically has a thermal conductivity of about 1 Btu/hr-ft-°F.
Here is the link to the document