I am in disagreement with some of my colleagues as to whether to take credit for insulation on a propane dehydrator vessel for the fire sizing case. The vessel is insulated and I have selected an environment factor F as per table 5 of API Std 521 in accordance with the insulation type and thickness. This has the effect of reducing the PSV size from a J orifice to an E.
Section 4.4.13.2.7.1 of API Std 521 states that credit is "typically not" taken for thermal insulation because it does not "usually meet" fire protection requirements. This seems like pretty imprecise language for a standard.
I have taken credit for insulation for fire sizing and fire is the only sizing case. My argument is that the purpose of the relief valves is to avoid BLEVE of these vessels long enough that personnel can safely evacuate. Realistically the insulation will stay functional during the time it will take to evacuate.
Part of the API criteria for considering whether insulation and jacketing will stay functional during a fire is that it is not dislodged from water streams or compromised from high temperature. By this time, any personnel in the area will be long gone. If personnel choose to fight the fire, that is an assessed risk outside the normal design. No size of PSV will prevent the vessel wall from failing in a sizeable fire and resulting in an explosion.
It might seem easy to just put on valves sized with no credit for insulation, but there is a high cost to going with larger relief valves, mostly in the increased size of flare pipe and associated piperack steel.
Any thoughts or interpretations of the PSV sizing standard?
Section 4.4.13.2.7.1 of API Std 521 states that credit is "typically not" taken for thermal insulation because it does not "usually meet" fire protection requirements. This seems like pretty imprecise language for a standard.
I have taken credit for insulation for fire sizing and fire is the only sizing case. My argument is that the purpose of the relief valves is to avoid BLEVE of these vessels long enough that personnel can safely evacuate. Realistically the insulation will stay functional during the time it will take to evacuate.
Part of the API criteria for considering whether insulation and jacketing will stay functional during a fire is that it is not dislodged from water streams or compromised from high temperature. By this time, any personnel in the area will be long gone. If personnel choose to fight the fire, that is an assessed risk outside the normal design. No size of PSV will prevent the vessel wall from failing in a sizeable fire and resulting in an explosion.
It might seem easy to just put on valves sized with no credit for insulation, but there is a high cost to going with larger relief valves, mostly in the increased size of flare pipe and associated piperack steel.
Any thoughts or interpretations of the PSV sizing standard?