The building was built in 1960s. The suspended slab is 140 thick and the areas near to the balcony was damaged becuase of magnesite flooring. About 50-80mm top of slab were excavated to eliminate magnesite. Top steel bars were exposed in living room and top steel bars in the kitchen were cut.
Tempory props were put under the damaged areas and between the cracks. And the balconies also were temporary props. The crack width is about 1 to 1.5mm.
The slab were poured in one piece with the length shown in the sketch is 12m by 9m.
All the wall is load bearing wall. We scan the reinforcement and I've done some draft calculation and it seem that there is enough reinforcement.
My question is:
- The steel bars must have yield strength < 350MPa ?
- The cracks were formed due to the damage magnesite areas in which reduce the slab stiffness near the supports and combined with shrinkage crackings to joint all cracks. The long bottom crack in the middle is about 1.5mm and is due to the damage magnesite area ?
- The top crack ruuning along the wall is flexural crack or shrinkage crack ?
Tempory props were put under the damaged areas and between the cracks. And the balconies also were temporary props. The crack width is about 1 to 1.5mm.
The slab were poured in one piece with the length shown in the sketch is 12m by 9m.
All the wall is load bearing wall. We scan the reinforcement and I've done some draft calculation and it seem that there is enough reinforcement.
My question is:
- The steel bars must have yield strength < 350MPa ?
- The cracks were formed due to the damage magnesite areas in which reduce the slab stiffness near the supports and combined with shrinkage crackings to joint all cracks. The long bottom crack in the middle is about 1.5mm and is due to the damage magnesite area ?
- The top crack ruuning along the wall is flexural crack or shrinkage crack ?