There is a free program called Life365 available with which you can calculate the life of your pile. Just search
and download the software and manual.
The durability of a pile is hinged on how corrosive the environment generally represented by the chloride concentration. Thereafter by how the rebar protected (naked, epoxy coated, stainless steel), cover to the rebar and concrete mix (mostly on how much void or w/c ratio). Cement replacement is used is considered and so any corrosion inhibitor applied.
The life365 has been for some years and there is a ACI committee on it too.
It is a definitive design procedure on the life expectancy on reinforced concrete. I used to program the diffusion theory myself and found good agreement with this program so I have been using for years ever since. Done this with piles too and all sorts of RC infrastructures.
I have seen RC structures that disintegrated after 12 to 15 years and Life365 can model it. So I can recommend that this is not olny mathemically rigorous but has been proven accurate in the field.
Specific to your pile section socketed into rock you have to decide on its chloride concentration and then test different concrete cover to see how long the pile can last. There is a lot of examples available to help you to decide on the chloride concentration. Being socketed into rock your grouted pile section should last longer than the normal pile I would have thought as the section should be sealed when properly constrcuted. This means you are justified to use a chloride concentration lower than expected. Your soil report, ground water analysis and the site proximity to the sea should help you to establish source and concentration of the chloride. The Life365 is the structural calculation to back you up on your decision. In general concrete degraes due to caboration and chloride able diffuse through concrete to reach a concentration level to cause the onset of corrosion. The time taken is the life of your pile.