Electrical
- Aug 21, 2009
- 16
hi all ,
I found during my commissioning work in substation that
Interposong CT used with an Ameter has the following class
0.5FS2( Burden 5 VA) but the required one as per drawing is 0.5FS5 with burden 2 VA. they match in other ch's
Ratio 1/1 , Rct = 1.3 ohm etc.contractor engineer told me
that will not affect! but I would like to ask experts
before accepting that especially , our design and planning
division replay will spend long time.
there is somthing I would like to mention that IPCT is
connected to Main CT used for( protection+ metering )
Ratio 1200/1 Class x which exist in GIS.
question now , is there any problem using that ipct ?