Hi there all,
I’ve been asked to justify the repair/replacement of lagging on Steam lines going from one part of the site to another. Its external and crosses a bridge. They’re old enough lines and there’s loads of lagging wrecked.
I’ve had a contractor come in and give me costs for replacing the lagging… so I just need to find the ROI.
I’m having a bit of bother finding the Costs of the Steam losses. I’m trying to determine the cost / meter / hr of the losses.
I think I’ve been able to find my Steam losses:
(taken from example 2.14.5 in this page: )
= (3.6*Q*L)/hfg
Total length (L)136.4
w/m (Q) 3699
hfg 2015.1
ms (kg) 901.373113
=(3.6*3699*136.4)/2015.1
=901.37kg/hr of Steam
(Can I work out my cost per meter with this?)
I found w/m below from this program: ( )
= 3699
I found hfg (kJ/kg) from the steam tables (evaporation at 9Bar): = 2015.1
The program above also can work out the actual cost of the losses per meter but the figures don’t look right
Here’s what I put in to the program in the Energy/cost of energy page (changed units to SI on menu bar):
Pipe = Horizontal
System Units = ASTM C585
Fuel Type = Natural Gas
Heat Content (calorific value of the Gas) = 3.826E+07
Fuel Cost = 0.26$ / m3 (currently £24/MWh of Gas at present)
Efficiency (of boiler) = 81.20%
Process Temp (Stem Temp) = 175.4
Ambient Temp = 9DegC
NPS Pipe Size (Pipe size) = 250mm
Wind Speed = 4.5m/s
Annual Operation = 8765hrs/yr
Soo… you’ll see it spits out that having a bare pipe costs 0.98 ($/m/yr) (don’t think the currency matters) and the W/m = 32430000
Then if I multiply the cost by the meterage = £0.98*136.4m= £133.67 for the whole line / year.
I don’t wanna show this as it doesn’t sound right since the ROI would be massive. Soo… a 136m length of 250mm Steam line at 175Deg C is only costing us £133/yer in lost heat?... doesn’t sound right??
Can you see where I’m going wrong?... maybe I’m going about this the long way.
What does the w/m mean… is this watts/meter?
Sorry this is soo long... thanks in advance for your help.
Alka
I’ve been asked to justify the repair/replacement of lagging on Steam lines going from one part of the site to another. Its external and crosses a bridge. They’re old enough lines and there’s loads of lagging wrecked.
I’ve had a contractor come in and give me costs for replacing the lagging… so I just need to find the ROI.
I’m having a bit of bother finding the Costs of the Steam losses. I’m trying to determine the cost / meter / hr of the losses.
I think I’ve been able to find my Steam losses:
(taken from example 2.14.5 in this page: )
= (3.6*Q*L)/hfg
Total length (L)136.4
w/m (Q) 3699
hfg 2015.1
ms (kg) 901.373113
=(3.6*3699*136.4)/2015.1
=901.37kg/hr of Steam
(Can I work out my cost per meter with this?)
I found w/m below from this program: ( )
= 3699
I found hfg (kJ/kg) from the steam tables (evaporation at 9Bar): = 2015.1
The program above also can work out the actual cost of the losses per meter but the figures don’t look right
Here’s what I put in to the program in the Energy/cost of energy page (changed units to SI on menu bar):
Pipe = Horizontal
System Units = ASTM C585
Fuel Type = Natural Gas
Heat Content (calorific value of the Gas) = 3.826E+07
Fuel Cost = 0.26$ / m3 (currently £24/MWh of Gas at present)
Efficiency (of boiler) = 81.20%
Process Temp (Stem Temp) = 175.4
Ambient Temp = 9DegC
NPS Pipe Size (Pipe size) = 250mm
Wind Speed = 4.5m/s
Annual Operation = 8765hrs/yr
Soo… you’ll see it spits out that having a bare pipe costs 0.98 ($/m/yr) (don’t think the currency matters) and the W/m = 32430000
Then if I multiply the cost by the meterage = £0.98*136.4m= £133.67 for the whole line / year.
I don’t wanna show this as it doesn’t sound right since the ROI would be massive. Soo… a 136m length of 250mm Steam line at 175Deg C is only costing us £133/yer in lost heat?... doesn’t sound right??
Can you see where I’m going wrong?... maybe I’m going about this the long way.
What does the w/m mean… is this watts/meter?
Sorry this is soo long... thanks in advance for your help.
Alka