EnergyProfessional
I'm designing a slab-on grade radiant system, and haven't done that before. I may be overthinking this, but got deep into calculating the actual heat loss to the ground and outside. The uponor design documents consider "Downward losses"significant, bit refer to their software to actually calculate them. I used THERM to model what is going on. I attached a picture of how the slab looks like 50 ft in, and the outside 50 ft along with the isotherms. The slab will have 4" horizontal XPS, and 2"vertical XPS insulation. The building will be in WI with -15°F OAT design temp and ~55°F indoor temp. I assume soil temp of 50°F in 30'depth.
I use Trace to calculate the load, but doubt it has specific provisions to calculate what i seem to overthink.
With these conditions I calculated U/R values for every 10 ft. of slab. Not surprisingly the R-values get very large as i move past the first 10 ft. The R-value is calculated from the heat loss from the slab. Both ground temperature and OAT are important. near perimeter, OAT is dominant. away from perimeter, I only lose heat to the soil. If i didn't have in-floor radiant, this would not be much (55°F space vs. 50°F ground at 4" insulation). it may not be intuitive, but since I deal with two heat-sinks (ground and outside) my U/R value changes with different temperatures. these R-values i can use to calculate heat loss (regardless of if heat goes outside or to the ground)
My theory is:
- when calculating space load I don't take into account any floor losses since the floor is warmer than space temp. (being conservative, I could just
include it)
- when calculating boiler and system size I need to add the floor losses including the fact the floor will be 100°F (and not just space temp)
- the sizing of the radiant heating (spacing of tubes, flow etc. ) would be done by manufacturer. Unless i come up with a better method
I think what I'm asking for is any advice to really understand and calculate the heat losses, size the system and radiant flooring. If any books are recommended, buying them is not a problem.
Amazon has some, but most seem to be for DIY or for installation.
there doesn't seem much concrete information. Even ASHRAE "HVAC Equipment and systems" chapter 6 doesn't really say much. I think most is written about electric radiant heating, wall and ceiling panels, and radiant cooling. but hydronic in-slab heating seems neglected, even if it is the most common.
Another thing I need to consider if i need to have some sort of hydronic Unit Heaters by the Overhead doors (this is a garage) for when the doors open assuming the radiant heating doesn't react quickly. Comfort is not an issue, but don't want sprinkler pipes to freeze if a door stays open long.
any advice appreciated.
My theory is:
include it)